Bonding switches to their enclosures.

Status
Not open for further replies.
Today at work, I got into a discussion with a co-worker about the question of whether or not you are required to bond a snap switch (or any other type of switch for that matter) to the metal enclosure in which it is installed.

He said that it was not a requirement. I agreed that it had not been a requirement in the past, but that at some point (I thought it was the 2002 NEC), all that changed, making it now a requirement to bond switches to their respective enclosures.

So far, I am coming up with: I am wrong. If that is the case, I am willing to admit it. But, I could have sworn that the rules changed at some point.

What is puzzling to me is the idea that receptacles must be bonded to their enclosures but not switches. I don't see the difference functionally.

Anyone have any ideas?
 
404.9(B)

1014160333_2.gif


Roger
 
This code change involved grounding metal faceplate's. Roger's post shows the different ways that this can be achieved. A grounded metal box is permitted to ground the switch through the two 6-32" mounting screws. A bonding jumper to the box is not required.
 
In most cases your bonding the exterior structural thats make up the outer structure of the chassie. While designed isolated from the switching operation, it is a potential in a failure, and the bond is installed, to aid in the tripping of the circuit breaker, and help carry away the potential difference.
 