There is no grid power on site at all.
There is a generator in a shed, and a 200 Amp main panel about 120 feet away in a separate building.
The GenSet has a bonded neutral.
If I install a non-fused disconnect in the shed where the generator is, do I......
Bond the neutral at the main panel?
Bond it at the disconnect? It isn’t set up for that, so I may need to get a SE Rated panel instead.
Or, bond it both places? 250.30(A)1 exception 2?
Conduit is PVC.
Thanks for any and all assistance.