Just recently on a job I am working on I noticed a possible mistake in the drawings. They show 4-4/0 & #2gr off of a sw. gear that is 600A 277/480v
fed off of the seconday side of the power co. utulity xfmr. the secondary V is 277/480v 4 wire out of the utility xfmr so their must be a bonded neutral in this xfmr. So back to the 4 4/0 & #2gr out of the gear, this goes into an ATS sw. that gets generator pwr from an existing 277/480v genset and backup pwr sw. gear. The load of the ATS then feeds a 150KVA xfmr with what is drawn as 4-4/0 & #2gr again. Yet the xfmr is a 480v delta to 120/208v Y.
I brought this to my boss's attn. and he said that we need to bond the line side neutral (277/480v-N), the load side neutral (120/208v-N) & then bond them to ground also. This just doesn't seem right at all... would there be any damaging effects as a result of this? I would like to know for my own knowledge so I don't make the same mistake in the future if that was the case.
fed off of the seconday side of the power co. utulity xfmr. the secondary V is 277/480v 4 wire out of the utility xfmr so their must be a bonded neutral in this xfmr. So back to the 4 4/0 & #2gr out of the gear, this goes into an ATS sw. that gets generator pwr from an existing 277/480v genset and backup pwr sw. gear. The load of the ATS then feeds a 150KVA xfmr with what is drawn as 4-4/0 & #2gr again. Yet the xfmr is a 480v delta to 120/208v Y.
I brought this to my boss's attn. and he said that we need to bond the line side neutral (277/480v-N), the load side neutral (120/208v-N) & then bond them to ground also. This just doesn't seem right at all... would there be any damaging effects as a result of this? I would like to know for my own knowledge so I don't make the same mistake in the future if that was the case.