Re: Bonding utility secondary raceway
Originally posted by dnbob:
So am I correct that it is necessary to bond the metallic raceway to the neutral in the meter can?
Bond it to either the meter can or to the neutral.
If there is a open terminal to connect it to the neutral that would be a more direct connection.
MGN is what you are calling the neutral, IMO it is MGN until you bond it at the service panel, at that point you have a grounded conductor and a grounding conductor.
That said I like Tom's suggestion of non metallic flex, nothing to bond.
[ April 10, 2004, 06:20 AM: Message edited by: iwire ]