Good afternoon everyone,
I am conducting a service change and installing a new 200 amp underground fed service. This will be a service disconnect meter enclosure due to the fact that the panelboard is more than 10 feet away from the meter enclosure. My question is this: Can I run a continuous grounding electrode conductor from the meter enclosure to my two ground rods and then bond tge gas and water line with the same continuous conductor? It would use much less wire and save a bunch of time to be able to do it this way. Rather than going back to the panel board to bond the gas and water. I don’t see any reason in the NEC why I can’t. Just seems unconventional and wanted to make sure before I did it.This is a residential structure. Single family dwelling. Thanks for any help.
I am conducting a service change and installing a new 200 amp underground fed service. This will be a service disconnect meter enclosure due to the fact that the panelboard is more than 10 feet away from the meter enclosure. My question is this: Can I run a continuous grounding electrode conductor from the meter enclosure to my two ground rods and then bond tge gas and water line with the same continuous conductor? It would use much less wire and save a bunch of time to be able to do it this way. Rather than going back to the panel board to bond the gas and water. I don’t see any reason in the NEC why I can’t. Just seems unconventional and wanted to make sure before I did it.This is a residential structure. Single family dwelling. Thanks for any help.