mkgrady
Senior Member
- Location
- Massachusetts
I’m changing a residential service entrance from a 200 amp overhead to underground. Because the underground will enter the basement not near the existing main panel I am installing a main breaker at the new meter location. This of course will require four conductors be run from the new main to the existing panel and the panel will be converted to a sub-panel.
My question is about the existing bond wire to the water line. The water line is not a grounding electrode. It is a plastic water line into the house. The bond wire is run from the metal pipe to the old main panel and connects to neutral. Am I correct that this wire does not have to be extended the the new main, and am I correct that it needs to just be moved to the equipment ground bar of the existing panel?
On a similar subject, what gets bonded when there are multiple runs of plastic and metal water pipes all over a house. In other words the metal pipes are not continuous. I see this on residential jobs that have had multiple renovations over time.
My question is about the existing bond wire to the water line. The water line is not a grounding electrode. It is a plastic water line into the house. The bond wire is run from the metal pipe to the old main panel and connects to neutral. Am I correct that this wire does not have to be extended the the new main, and am I correct that it needs to just be moved to the equipment ground bar of the existing panel?
On a similar subject, what gets bonded when there are multiple runs of plastic and metal water pipes all over a house. In other words the metal pipes are not continuous. I see this on residential jobs that have had multiple renovations over time.