Steel well casing is 25+ feet from closest point of the inside pool surface, but is within 6' of the bonded pool deck. I could see how, in theory, but kinda of a stretch, a dripping wet kid could chase a ball and have one foot on deck while touching casing.
Well casing houses inverter driven variable speed pool pump which are known to throw off transients to ground. Well casing is also bonded to the residence through UFER and ground rods through the intersystem bonding connector.
Is bonding the casing to the pool via the deck steel inviting more harm than good? In this case, it seems to me the possibility of the well casing becoming energized is high and that would lead to pool becoming energized.