Re: Bonding with platic water pipe coming in
Pierre, it is not the intent of the NEC to require the water line to carry fault current. However, it will indeed carry fault current if the neighborhood is connected with a metallic water system. The fault current can flow through the GEC to the water line, through the metallic water system to your neighbor's home, through his GEC, through his service drop or lateral, and back to the transformer.
This will not happen to any great amount unless you have an open neutral since
most of the return current will take the path of the phase conductors.
One of the problems we have had with old neighborhoods is to have an open neutral with the old ACSR conductor in a triplex service drop. It would go for years with no problems and would be found with routine service work or a service upgrade. We used to use #6 ACSR for the neutral of a #4 Al triplex and the galvanizing would be pitted. That would allow the steel to rust and separate, then the neutral would break. Needless to say, every time we come across an old 4/6 triplex, we replace it.
Tom, the current carrying ability of a metallic water line is immense with the water in the line. The water will act as a heat sink and, under fault conditions, the current will not be there for a long time unless you are waiting for the electric utility's transformer fuse to let go.