SceneryDriver
Senior Member
- Location
- NJ
- Occupation
- Electrical and Automation Designer
I seem to be missing the part of 250 that clearly states that if one end of an EMT conduit run (feeder, not service conductors) is in a field-punched, non-concentric KO, it's OK to use reducing washers on the other end of the conduit run without the use of a bonding bushing.
For reference:
-120/240V single phase feeder
-Reducing washers on the "supply end" of the conduit run
-Ground wire (sized for the feeder) pulled in and landed in the non-concentric KO's enclosure.
Ironically, the concentric is still in place, but we used reducing washers because the concentric KO on the Square D fused switches are terrible and very weak. I'm being told we need a bonding bushing at reducing washers end.
I've seen the handy flowchart that floats around on this forum, but the version I have doesn't cite code sections and I can't find the above. I really wish it was made clearer and easier to grasp.
SceneryDriver
For reference:
-120/240V single phase feeder
-Reducing washers on the "supply end" of the conduit run
-Ground wire (sized for the feeder) pulled in and landed in the non-concentric KO's enclosure.
Ironically, the concentric is still in place, but we used reducing washers because the concentric KO on the Square D fused switches are terrible and very weak. I'm being told we need a bonding bushing at reducing washers end.
I've seen the handy flowchart that floats around on this forum, but the version I have doesn't cite code sections and I can't find the above. I really wish it was made clearer and easier to grasp.
SceneryDriver