resistance
Senior Member
- Location
- WA
Got a red tag today because we bonded the gas line from a sub-panel. Not sure why thats a problem. He said it needs to run back to the main? Code reference please.
Standard Blk pipe!What kind of gas pipe, CSST? Regular old black pipe does not require a separate bonding connection by the NEC. CSST may have specific requirements from the manufacturer.
Standard Blk pipe!
I realize that many narrow that section to branch circuit EGC, service , or GE. However, a subpanel EGC is just as viable. 250.104(B) does not say branch circuit. It says the EGC of the circuit likely to energize the pipe... and then most assume that is the branch circuit of the appliance connected to the pipe. Well the feeder that supplies that branch circuit is also part of the circuit likely to energize the pipe, so just as viable... and even more so for non-electrical gas devices.On occasion I will encounter a hard pipe gas system where the piping supplies only appliances that have no electrical circuits (fire place, wall heater (no blower), etc).
In that case, as I read 250.104(B), you would need to bond back to the service or grounding electrode system.
Well the feeder that supplies that branch circuit is also part of the circuit likely to energize the pipe, so just as viable...
On occasion I will encounter a hard pipe gas system where the piping supplies only appliances that have no electrical circuits (fire place, wall heater (no blower), etc).
In that case, as I read 250.104(B), you would need to bond back to the service or grounding electrode system.
Not suggesting it applies to everything. But let's look at this particular issue logically.I disagree with your 'everything is part of the circuit' theory when it comes to applying the NEC.
When the NEC refers to 'a circuit' it does not mean the entire circuit from source to load. (IMO)
The size the AHJ approves. Of course that may be determined after you install one that is too small...The million dollar question is what size conductor do you require?
The size the AHJ approves. Of course that may be determined after you install one that is too small...
This is the requirement from the 2015 International Fuel Gas Code and the same requirements is in the International Residential Code.
SECTION 310 (IFGS) ELECTRICAL BONDING
On occasion I will encounter a hard pipe gas system where the piping supplies only appliances that have no electrical circuits (fire place, wall heater (no blower), etc).
In that case, as I read 250.104(B), you would need to bond back to the service or grounding electrode system.