B Bryan robertson Member Location Fresno California usa Feb 13, 2019 #1 I have a inspector telling me I haft to bond my emt chases. These chases are going thru a fire wall for data wires. Is this a code I don’t know about?
I have a inspector telling me I haft to bond my emt chases. These chases are going thru a fire wall for data wires. Is this a code I don’t know about?
S Strathead Senior Member Location Ocala, Florida, USA Occupation Electrician/Estimator/Project Manager/Superintendent Feb 13, 2019 #2 Bryan robertson said: I have a inspector telling me I haft to bond my emt chases. These chases are going thru a fire wall for data wires. Is this a code I don’t know about? Click to expand... News to me. "May become Energized, is the applicable wording I think of. So he would have to explain how they could become energized.
Bryan robertson said: I have a inspector telling me I haft to bond my emt chases. These chases are going thru a fire wall for data wires. Is this a code I don’t know about? Click to expand... News to me. "May become Energized, is the applicable wording I think of. So he would have to explain how they could become energized.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Feb 13, 2019 #3 Short sections of raceway used as sleeves are not required to be bonded. Ask for a code reference.