Re: Bonding
OK what do you need to bond?
Even with an ungrounded delta service the raceways and enclosures are still bonded, its just the service itself is not bonded.
Also there is a big difference between an ungrounded delta and corner grounded delta. You are allowed to operate a system ungrounded under certain conditions see section 250.21.
Section 250.20 B lists what systems have to be grounded, I bet your irrigation system requires grounding.
You state bonding, do you mean bonding to a grounding electrode system?