bonding

Status
Not open for further replies.

supercell

New member
Which 250 table do you use for sizing the bonding wire wrapped around sealtight when going from the panel to the transformer. And what's the purpose. I can't really get a clear understanding from the code book.
 
Re: bonding

This would be an equipment bonding conductor and sized from Table 250.122. As far as wrapping the conductor around the sealtight I have been taught that it is a bad practice. Some say it is a violation of 250.102(E). At an IAEI ground seminar, I asked this question of Mr. Phil Simmons, former chairman of CMP5, and his answer was that it is not a violation to wrap the bonding conductor around the sealtight.
Don
 
Re: bonding

Don,

I'm sure you're right :D ....as long as the length of the conductor doesn't exceed 6'.

What I wonder is why it isn't installed inside the raceway. :confused:
 
Re: bonding

An engineer once told me it let you "visually confirm that the EGC was intact and connected". I have seen it in a lot of industrial locations, but it seems after a while the insulation starts falling off and the wire gets ratty. Appleton and others make sealtite fittings with a lug for doing this.

Personally, I don't like it, but specs are to be followed...

Mike
 
Re: bonding

I have seen pumps that come with no ground stud inside the motor box. Putting the ground wire along side the flex is the only practical way to bond such a beast.
 
Re: bonding

Dave,
The plant standard where I work calls for rigid conduit, internal equipment grounding conductor and an external bonding jumper around the sealtight connection to the motor.
Don
 
Re: bonding

We should be seeing this when the conduit does not have an internal EGC and where the flex does not have supports within 12" of each termination.
I expect that many times this bonding jumper is not installed when it should be.
Don
 