Re: bonding

Originally posted by DPJ44:
well, 250-4 says anything that can become energized shall be bonded
Not really. It says things that are likely to become energized.

I can't see why a person would bond something that is never going to get energized.
 
Re: bonding

DPJ44, 250-4 (pre 2002 NEC by your use of the dash) is a general rule, summary so to speak. This is pretty much the same (if not identicle) in other code cycles.

See 250.104 for more specifics.

Roger

[ June 28, 2005, 08:05 PM: Message edited by: roger ]
 
Re: bonding

Just about anything "likely" to energize metal has electricity fed to it, and the supplying circuit will have an EGC, which is adequate to provide the necessary bonding.
 