F francisco New member Jul 15, 2004 #1 A cable intended to go to "XO" on a transformer coming from building ground. Can it be bonded at any other location (j-box, bond bushing, etc) other than the transformer?
A cable intended to go to "XO" on a transformer coming from building ground. Can it be bonded at any other location (j-box, bond bushing, etc) other than the transformer?
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Jul 15, 2004 #2 Re: bonding Yes. See section 250.30(A). Its a bit long to paste here.