250.146(B) Contact Devices or Yokes. Contact devices or yokes designed and listed for the purpose shall be permitted in conjunction with the supporting screws to establish the grounding circuit between the device yoke and flush-type boxes.
EMT is the EGC! and it is allowed to bond the box.By Don: If you splice in the box or install a device in the box, you must bond the EGC to the box
in your opinion, does that supercede 406.3 that deals specifically with receptacles?Originally posted by iwire:
Check out 250.146(B)
250.146(B) Contact Devices or Yokes. Contact devices or yokes designed and listed for the purpose shall be permitted in conjunction with the supporting screws to establish the grounding circuit between the device yoke and flush-type boxes.
i think what they are saying is IF you run an EGC IN the EMT, THEN you must bond it to the box when you splice or install a device..Originally posted by hurk27:
EMT is the EGC! and it is allowed to bond the box.By Don: If you splice in the box or install a device in the box, you must bond the EGC to the box
This is only describing how to make a connection between more that one EGC. and or one EGC to a grounded box. Or to a non-grounded box that was fed by an non grounded race-way method I.E. PVC conduit, NM, FMC.Where circuit conductors are spliced within a box, or terminated on equipment within or supported by a box, any separate equipment grounding conductors associated with those circuit conductors "shall be spliced" or "joined within the box" or "to the box with devices suitable for the use".