I have a set of plans that calls for an auto-transformer to boost 208 to 480. 3Ø 10hp 11.2A. I am well aware if this was possible it would take 2 trannies but none of my charts show this as being remotely doable.
Before I fire off a RFI, am I missing something here?
Thanks
Assumptions:
1. The input is 208Y/120.
2. The desired output is 480 delta.
Any autotransformer use on a wye supply would be most understandable if each autotransformer were wired line to neutral on its input.
You would need 3 transformers for this configuration, since a "open wye" cannot drive a true three phase load.
Each autotransfomer would raise 120 to 277, producing a 480Y/277 output.
A delta load would not have to make use of the neutral, but the output would necessarily be grounded wye since the windings do not provide isolation.
Another alternative would be to use two 208 to 480 autotransformers, which would produce an open delta where the "neutral", if used, would not be a true neutral and the resulting delta would not be symmetrical with respect to ground.
Or you could use three such transformers to produce a symmetrical-to-ground delta output which would be a triangle rotated with respect to the original delta triangle (in the schematic, not the phasor diagram). Not sure how the code would treat that one.
It is not clear to me that using an autotransformer for a step-up ratio greater than 2 would be a good engineering and cost solution.