Boost 240 to 277 Single Phase.

Status
Not open for further replies.

xlx

Member
Hello everyone. I don't believe that I have ever posted here before but I am stuck and need some help. I am considering using an auto-transformer to boost a single phase 240 volt circuit for a sign to 277 volts. Section 210.9 appears to prohibit this. Is there any way to make it work? I am feeding from a 120/240 volt single phase supply so I can't connect the service neutral to my auto transformer. Does the 277 volt branch have to have a grounded neutral? Thanks for your help!
 
I don't believe that I have ever posted here before . . .
You have, four times. Welcome back. :)

Section 210.9 appears to prohibit this.
I agree. Now, if you were stepping 120v to 277v . . .

Is there any way to make it work?
As I see it, a standard 240-277 transformer. Plus bonding the secondary, making it the grounded conductor.


If I may ask, what's the load?
 
Thanks Larry! It looks like I will be buying a standard transformer! 120 is not practical as the run is +- 500' and the sign company has specified a 3% voltage drop. The load is a large sign with (24) 250 watt metal halide ballasts. They run about 1.1 amps each at 277. Add a control circuit, A clock and some overhead and I plan on providing 40 amps.
 
One more thing: with such a long run, you should transmit the highest voltage you can for the least voltage drop, so I suggest boosting the voltage as close to the source as you can, and not at the load end.

Added: For that matter, if you can, step up the 240v at the source to, say, 600v for the long run, and then from 600v down to any voltage you like at the load, even 120/240v. Don't forget to bond at the load end.
 
Last edited: