I hope I'm right on this one. (I'll try to keep it short)
Today I was engaged in a disagreement with a "building staff engineer'' about a piece of equipment they called my shop out to move to a new location.
The piece of equipment is a 3 phase 240vac paper shredder made in europe.
The building only has the means to supply 208 vac.
The building staff engineer built a boost station with 2 single phase transformers and claims that the european company told him how to hook it up and what it required.
I insisted that it was wired in error (at least to American standards). I told him in order to boost 208(3phase) to 240(3phase) he needed 3 single phase transformers not 2.
Am I correct, or do I have to eat crow.