Boost Transformer 208 to 480 Grounding not bonding

Status
Not open for further replies.

Fordean

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
Boosting 208 to 480 for machine testing. Don't need a neutral. Transformer is 150 feet from Service. Per previous discussion, We agreed not to bond Xo to ground. Since it is not being used in this case. Question is, Do I need to still run ground wiring to nearest steel, Or is the existing ground path thru conduit (has ground conductor in pipe) sufficient, Or since I am not using Xo, There is no need to bond to steel
Code number would work for me, Looking as we speak.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Its 208 wye to 480 Delta
So there is no X0 on the secondary side. Your choices are corner ground on the 480 side or ungrounded with a ground detector. Since this is being used for testing I would think that you would want to use a grounded system. IMO this is not the best transformer for your application, I would use a Delta/Wye.
 