Re: boost transformers for motors.
codeunderstanding
I did the following calculation.
OCPD for a motor 430.52
17 amps X 2.5(breaker) = 42.5 amps
a 50 amp breaker is max motor OCPD
17 amps X 1.75(TD fuse) = 29.75 amps
a 30 amp time delay fuse would be OK
OCPD for an autotransformer 450.4(A)
if the boost is 24v 500va/24v = 21 amps flc
21 amps X 1.25 = 26 amps a 30 amp fuse or
breaker would be OK
if the boost is different, change the calculation to 32v or whatever and check.
For a 24 volt boost transformer it seems that you could use a 30 amp fuse as both motor B-C, S-C, & G-F protection and transformer protection.
Look at it and see what you think.
Jim T