hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
Attached sketch i have panelboard breaker feeding control panel which feed three booster pumps each 15HP 208V three phase and manufacturer says each has FLA of 46.2A.
The control panel internal manufacturer provided 80A fuse for each booster pump. Designer says the fuses are for overload protection.
I am not sure if I am using the correct code section for sizing the feeder breaker supplying the control panel which is NEC 2017 Section 409.21(C) or not. According to that, if there is no short circuit and ground fault protection in control panel then to use 430.52 and 430.53 as applicable. Otherwise if short circuit and ground fault protection is provided then use 409.21(C). The internal 80A fuse according to designer is for overload protection
So my question is would one use 409.21(C) or 430.52 and 430.53? Does fuse provide short circuit and ground fault protection or not if it provides overload protection?
The control panel internal manufacturer provided 80A fuse for each booster pump. Designer says the fuses are for overload protection.
I am not sure if I am using the correct code section for sizing the feeder breaker supplying the control panel which is NEC 2017 Section 409.21(C) or not. According to that, if there is no short circuit and ground fault protection in control panel then to use 430.52 and 430.53 as applicable. Otherwise if short circuit and ground fault protection is provided then use 409.21(C). The internal 80A fuse according to designer is for overload protection
So my question is would one use 409.21(C) or 430.52 and 430.53? Does fuse provide short circuit and ground fault protection or not if it provides overload protection?