Bootleg ground from neutral

Status
Not open for further replies.

Srv52761

Senior Member
Location
lowa
Occupation
Energy Manager
0BB24B07-C7C9-40E5-8BDF-F0014378C872.jpeg

Someone in a home improvement forum posted this picture and implied it was NEC approved in 2018 (probably meant 2017).
Maybe in conjunction with a gfci outlet?

Don’t remember ever seeing this before, nor read about it, either here or in any readings of the NEC. Have I missed this?
 
View attachment 2564922

Someone in a home improvement forum posted this picture and implied it was NEC approved in 2018 (probably meant 2017).
Maybe in conjunction with a gfci outlet?

Don’t remember ever seeing this before, nor read about it, either here or in any readings of the NEC. Have I missed this?
The only reason to do this would be to trick a testing device such as a Woodhead. It is considered wrong illegall and imoral. (Did I make it clear)
 
Maybe in conjunction with a gfci outlet?
No. In fact, when you use a GFCI in conjunction with ungrounded grounding receptacles, you are not supposed to connect any EGCs to any terminal or each other. Clip them off at the sheath.

This avoids a malfunctioning (line-to-housing fault) load from energizing another load.

Have I missed this?
It's normally seen in old work. Its only purpose is to fool inspectors who rely on plug-in testers.
 
No. In fact, when you use a GFCI in conjunction with ungrounded grounding receptacles, you are not supposed to connect any EGCs to any terminal or each other. Clip them off at the sheath.

This avoids a malfunctioning (line-to-housing fault) load from energizing another load.


It's normally seen in old work. Its only purpose is to fool inspectors who rely on plug-in testers.
I have a plug in tester that detects that. It must measure the resistance between the neutral and ground, and if it is too low, it flags it as a bootleg.
 
If you wire it like this it will make sure the breaker keeps it safe, the breaker on this circuit would not even stay on imagine that?
 

Attachments

  • justdont.jpg
    justdont.jpg
    128.2 KB · Views: 23
Wouldn’t be real good for inspections, it has to boot up every time you plug it in. I use it to check for high resistance ground's and other anomalies when troubleshooting.
 