but the white is on the black screw,To do that per code you also need to loop the bare over to the black wire.
The only reason to do this would be to trick a testing device such as a Woodhead. It is considered wrong illegall and imoral. (Did I make it clear)View attachment 2564922
Someone in a home improvement forum posted this picture and implied it was NEC approved in 2018 (probably meant 2017).
Maybe in conjunction with a gfci outlet?
Don’t remember ever seeing this before, nor read about it, either here or in any readings of the NEC. Have I missed this?
No. In fact, when you use a GFCI in conjunction with ungrounded grounding receptacles, you are not supposed to connect any EGCs to any terminal or each other. Clip them off at the sheath.Maybe in conjunction with a gfci outlet?
It's normally seen in old work. Its only purpose is to fool inspectors who rely on plug-in testers.Have I missed this?
but the white is on the black screw,
I don't think they're blackened; I think it's just the angle and lighting.Somebody's marked up the screws.
Ok.I don't think they're blackened; I think it's just the angle and lighting.
I have a plug in tester that detects that. It must measure the resistance between the neutral and ground, and if it is too low, it flags it as a bootleg.No. In fact, when you use a GFCI in conjunction with ungrounded grounding receptacles, you are not supposed to connect any EGCs to any terminal or each other. Clip them off at the sheath.
This avoids a malfunctioning (line-to-housing fault) load from energizing another load.
It's normally seen in old work. Its only purpose is to fool inspectors who rely on plug-in testers.
Care to share the brand and model ?I have a plug in tester that detects that. It must measure the resistance between the neutral and ground, and if it is too low, it flags it as a bootleg.
one up, two down.Somebody's marked up the screws. The EG is always on the side of the grounded conductor. At least all I can think of.