I have a plan submitted that wishes to add to an existing ground-mounted system. They already have a supply side tap for the existing system, but now they wish to add to the system, take one existing array and add a new array to it and connect it via POC at a breaker at the main service, but are leaving the rest of the existing system on the supply side tap. I have not seen this configuration before.
The Code states use of one OR the other:
(California Electrical Code) Article 690.64: "The output of a utility-interactive inverter shall be as specified in (A) OR (B)." (A) is supply side in accordance with 230.82(6); (B) is load side.
I feel that the interconnection should be one or the other. Any input on this condition would be greatly appreciated.
The Code states use of one OR the other:
(California Electrical Code) Article 690.64: "The output of a utility-interactive inverter shall be as specified in (A) OR (B)." (A) is supply side in accordance with 230.82(6); (B) is load side.
I feel that the interconnection should be one or the other. Any input on this condition would be greatly appreciated.