Boundaries of hazardous locations?

Status
Not open for further replies.

mesarush1

Member
Trying to determine where the boundaries of class 1 hazardous locations start/end. Need to price service and controls to an outdoor fuel processing plant where above ground fuel tanks and equipment for the transfer/mixing of fuel takes place. This equipment is located approx. 50' from where electrical service and controls are to be installed. Does the gear & install need to be explosion proof?
 

Rockyd

Senior Member
Location
Nevada
Occupation
Retired after 40 years as an electrician.
NEC 500.4(A) & (B) along with 500.5 will give you some guidance in gaining assistance as to area classification. Check with the project engineer.

500.4(A) Documentation All areas designated as hazardous (classified) locations shall be documented. This documentation shall be available to those authorized to design, install, mintain, or operate electrical equipment ant the location.
 