Per 501.15(B)(2) Exception 3 (2011 NEC): Boundary seals aren't required passing from a pressurized room into a C1,D2 area.
Is that exception only valid where the transition is immediate, or could the boundary seal be omitted in a conduit that leaves the room, travels some distance (lets say 10' - 20'), and then enters a C1D2 area?
The latter situation occurs regularly in the types of facilities I work in because a room may get pressurized due to impingement along 1 wall, but along the other walls conduits cross an unclassified area before going into the classified process area.
Per 501.15(B)(2) Exception 3 (2011 NEC): Boundary seals aren't required passing from a pressurized room into a C1,D2 area.
Is that exception only valid where the transition is immediate, or could the boundary seal be omitted in a conduit that leaves the room, travels some distance (lets say 10' - 20'), and then enters a C1D2 area?
The latter situation occurs regularly in the types of facilities I work in because a room may get pressurized due to impingement along 1 wall, but along the other walls conduits cross an unclassified area before going into the classified process area.