Forgive me if this has already been addressed, but I cannot find it by searching.
When installing a conduit seal between Div 1 and Div 2, and the conduit runs underground, the seal is permitted to be installed at the end that exits the ground if the boundary exists where the conduit is underground - 501.15(A)(4) Exception 2 I believe.
I'm not sure what to do if the same situation exists for Div 2 to unclassified. My thoughts are that if is good enough for Div 1 to Div 2, then it should be okay for Div 2 to unclassified, but the NEC does not specifically state this.
We have conduit entering the ground in a Div 2 area and installed underground for over 100' before exiting. The classification boundary exists a some point where the conduit is buried.
Thoughts?