brother
Senior Member
I'm a liittle rusty on some of my math. I know the NEC already gives cubic inches for most wire TABLE 314.16(B) ie.. #12 2.25 cube inches.
#12 THHN 0.0133 square inches TABLE 5 Chapter 9. I'm just curious if you had to convert to cubic inches from square inches, how would you do that??
I know measures volume height, length, width(cubic inches), and the other measures area length and width (square inches).
I was looking at that way I found the 'cable' fill in this post.
http://forums.mikeholt.com/showthread.php?t=126646
#12 THHN 0.0133 square inches TABLE 5 Chapter 9. I'm just curious if you had to convert to cubic inches from square inches, how would you do that??
I know measures volume height, length, width(cubic inches), and the other measures area length and width (square inches).
I was looking at that way I found the 'cable' fill in this post.
http://forums.mikeholt.com/showthread.php?t=126646
So if I had to size a box for this cable, how would one do it since boxes are in cubic inches. 2008 NEC 314.28 deals with #4 and larger for the 'pulls' that lets you know what size box to have by going off the largest size conduit and multiplying by 6 or 8. So what about cable that is not that big.brother said:I want to make sure Im doing this right in my calculation, there are 2 cables , each cable has 19 pairs. The o.d. on one cable is .603 inches. this is NOT square inches so I had to convert. I came up with using 1 1/2" emt conduit NEC 2008 TABLE 4 chapter nine.
Area= 3.14 * R(squared)
R= D/2
D= .603
R= .603/2=0.3015
Area= 3.14 X .3015 X.3015=.285
2X .285=.570 1 1/2 EMT conduit size needed. (0.631 sqr inches for emt)
since there are 2 cables and that means I have 2 conductors and have to use the 2 wires 31% fill.
Did I do this right?? I dont deal with multi cables much, just regular wire!