I am doing some old work and the outside walls only allow a 1.5" deep box. There are 1.5" deep boxes but using 14/2 and a device appears to violate the box fill requirement of section 314.16(b).
14/2 w/GND = 6 cu in
device= 4 cu in
total = 10 cu in
Oddly enough, one manufacture of steel boxes stated that you should count the device as one conductor, not two.
What are these boxes designed for. The metallic boxes I found are 7.5 cu in and the plastic box I found is 8 cu in.