Box fill above 4awg
dm9289
Industrial Maintenance Electrician
Pennsylvania
Industrial process repair/ maintenance Electrician
there are tables such as 314.16(A) and B for number of conductors 6awg and smaller with numbers for example 6 awg= 5sqin
What do you do for 4awg and larger
You would use the 6X and 8X rules for sizing the box. Here's an example from Mike Holt:
I have seen this graphic. I understand the examples with conduit. But is there no conductor fill limits
If you comply with the conduit sizes and box size ratios give then the conductor fill should already be accounted for in the calculations
Ok that's what I was getting at doing the sample problems from the library.
One more question I can see how we do length and width from above example, I don't believe the course addressed depth? I know it needs to handle the piping size but is there any other restriction
In the graphics the boxes only need to be deep enough to get the raceways in.