Hi, I have a quick question about box fill and common box volumes.


Working on our electrical rough-in, I just realized that some of the boxes I bought are a bit under-sized for where they will be used. I was also surprised that the wall box I planned to use most is listed as only 12.5 cu in. (2x3x2.5 in.)


What I find weird is that for this type of box, steel box with mounting clamp and internal NM clamps, this size is a common size at the home centers. Larger ones that are 2 3/4 and 3 1/2 deep are special order items. I would think with the limited use of a 12.5 ci box, the bigger ones would get used more, and also stocked at the store.


That made me doubt my calculations. But with a simple situation of a receptacle in the middle of a circuit run, I would have:
Two 14/2 nm > 4 cond > 8 ci
One recep > 2 cond > 4 ci
All ECG > 1 cond > 2 ci
Int clamps > 1 cond > 2 ci
Total: 16 ci required. Which means my 12.5 ci box is no good here. Yet it seems like there's plenty of space for this application.


So am I figuring this required volume right?


Any idea why a box with such limited application would be the one they stock while the larger versions are not stocked?


Thanks,
Keith
 
Your calcs look correct. Unfortunately this is a DIY question and although you have a permit and your state allows you to do the work, this is a professional forum for people who do this work as a living. Therefore I am closing this thread.

Forum Policy:

This site is designed for:
• Contractors
• Electricians
• Engineers
• Inspectors
• Instructors
• Other electrically related individuals
• This NEC Forum is for those in the electrical and related industries.

Questions posted that appear to be an attempt to gain assistance with an electrical installation will be removed. Forum rules prohibit us from assisting a person to perform or assist others to do electrical work who are not qualified. Mike Holt Enterprises and the Moderators of this Forum do not wish to place you and your family in danger, by allowing others to give you too little information to ensure that the installation is safe
 
Status
Not open for further replies.
Top