I am calculating box fill requirements for non-metallic sheathed cable in non-metallic boxes in residential construction.
(In California we still only enforce the '99 NEC, so it is article 370-16(b)(1) on page 193 of the '99 edition. I believe it is 314-16 (b) of the 2002 code)
The code says " a conductor, no part of which leaves the box, shall not be counted." Here is my problem: When the grounded conductors are pigtailed together, are any of those white wires counted? Same issue with the grounding and ungrounded conductors. They all enter the box, and no part of any of them leave the box, so does this satisfy the requirements? This seems as though ANY conductor would not be counted, as every wire would either be pigtailed or connected to a device in the box, therefore not leaving the box. The only conductor that would be counted would be those that pass through the box, effectively using the box as a raceway.
Any help?
Thanks -
Mike
(In California we still only enforce the '99 NEC, so it is article 370-16(b)(1) on page 193 of the '99 edition. I believe it is 314-16 (b) of the 2002 code)
The code says " a conductor, no part of which leaves the box, shall not be counted." Here is my problem: When the grounded conductors are pigtailed together, are any of those white wires counted? Same issue with the grounding and ungrounded conductors. They all enter the box, and no part of any of them leave the box, so does this satisfy the requirements? This seems as though ANY conductor would not be counted, as every wire would either be pigtailed or connected to a device in the box, therefore not leaving the box. The only conductor that would be counted would be those that pass through the box, effectively using the box as a raceway.
Any help?
Thanks -
Mike