Gategator37
Senior Member
Does box fill apply to NAC circuits?
The rules in Chapters 1 through 4 apply to the Chapter 7 Articles, unless the Chaper 7 Article says they don't. I don't see anything in Article 760 that says 314.16 does not apply.
760.3 Other Articles. Circuits and equipment shall comply
with 760.3(A) through (G). Only those sections of Article
300 referenced in this article shall apply to fire alarm
systems.
Derek,
I only read 760.3 as limiting the application of Article 300...not any of the other articles in Chapters 1 through 4.
3-154 Log #3660 NEC-P03 Final Action: Reject
(725.3)
_______________________________________________________________
Submitter: Donald A. Ganiere, Ottawa, IL
Recommendation: Revise text to read as follows:
Circuits and equipment shall only be required to comply with the articles or
sections listed in 725.3(A) through (G). Only those sections of Article 300
referenced in this article shall apply to Class 1, Class 2, and Class 3 circuits.
Substantiation: It appears that the intent of 725.3 is to exempt the installations
made under this Article from most of the rules in Chapters 1 through 4,
however the current wording does not specifically do that. The additional
wording will make it clear that only the articles and sections listed or
referenced in Article 725 apply to Article 725 installations.
Panel Meeting Action: Reject
Panel Statement: 90.3 provides the clarification requested in the proposal.
Number Eligible to Vote: 15
Ballot Results: Affirmative: 15
3-101 Log #1985 NEC-P03 Final Action: Reject
(725.3)
_______________________________________________________________
Submitter: Donald A. Ganiere, Ottawa, IL
Comment on Proposal No: 3-154
Recommendation: Proposal should be accepted.
Substantiation: 90.3 says that the rules in Chapters 1 through 4 apply to the
Chapter 7 Articles except as amended by the Chapter 7 rules. If it is the panels
intent to limit the application of the rules in Chapter 1 though 4 for Article
725 installations it must say so directly. Just putting a statement that says
“Circuits and equipment shall comply with the articles or sections listed in
725.3(A) through (G).” does not accomplish the objective. The first part of the
rule should be worded like the second part that says “Only those sections of
Article 300 referenced in this article shall apply to Class 1, Class 2, and Class
3 circuits.” The code wording is not consistent and is not clear what the actual
intent of the first part of the rule is.
Panel Meeting Action: Reject
Panel Statement: The proposed text would indicate that the rule in 90.3 does
not apply which is incorrect.
Number Eligible to Vote: 15
Ballot Results: Affirmative: 15
Comment on Affirmative:
STENE, S.: Acceptance of the suggested text would exclude compliance
with any other part of the NEC. The intent of 725.3 is to bring attention to very
specific sections of the NEC that are especially applicable but not to exclude
other requirements.