Box Fill

Status
Not open for further replies.

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
There is a fan rated pancake box with a 14/3 nm cable for a canopied fan with light. How many cu.in. do I use for box fill? Assume an external connector so no need to count it. Fan has 4 wires- white, black, red and green
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Assuming 14/3 WG your have (4) #14s requiring 8 cu inches. The four fan wires probably do not have to be counted per the exception to 314.16(B)(1) depending on how your interpret that exception which is likely why you asked it :).
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Assuming 14/3 WG your have (4) #14s requiring 8 cu inches. The four fan wires probably do not have to be counted per the exception to 314.16(B)(1) depending on how your interpret that exception which is likely why you asked it :).


Exactly my interpretation however Jeff Rodriquez who teaches code classes in our area and is a well respected teacher has sample tests that specifically state on the answer sheet that the equipment grounding conductor does not get counted based on the exception of the article you cited. I honestly don't see how he gets there. I have so much respect for his ability I am questioning myself here but I don't see it.

His answer is 6 cu. in

Exception: An equipment grounding conductor or conductors
or not over four fixture wires smaller than 14 AWG, or
both, shall be permitted to be omitted from the calculations
where they enter a box from a domed luminaire or similar
canopy and terminate within that box.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I disagree as well. The EGC that he is not counting does not "enter a box from a domed luminaire or similar canopy and
terminate within that box."


To me it is very clear however I think he is taking the first statement that says an equipment grounding conductor and stopping there. I see it as the egc can be omitted where they enter the box from the domed canopy
 

jumper

Senior Member
I the egc that can be omitted is that skinny little bare one that comes with some fixtures.

I am talking about the one that comes with a chandelier and you thread it through the chain with the fixture cord.
 
Last edited:

tkb

Senior Member
Location
MA
All of the items listed in the exception are for conductors that enter through the domed canopy. IMOo
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree, you count the conductors in the box without the fan in place. Hanging the fan does not magically remove the EGC from the box fill.
 