J jerseybillfromva New User Sep 5, 2024 #1 does a low volt signal wire have a box fill deduction? 800-110 says no for conduit fill but, nowhere can I find info concerning box fill
Ohm2 Member Location Washington Occupation Electrician Sep 5, 2024 #2 jerseybillfromva said: does a low volt signal wire have a box fill deduction? 800-110 says no for conduit fill but, nowhere can I find info concerning box fill Click to expand... I’m not sure there is one. But if you decide to use a box you should still consider the box size.
mikeames Senior Member Location Gaithersburg MD Occupation Teacher - Master Electrician - 2023 NEC Sep 5, 2024 #3 Box fill applies to chapter 3 methods unless specified so, no. 314.16(B)1 only goes to 18awg so there would be no volume allowance to calculate box fill with something like UTP cat 5/6. There are raceway fill issues if medium powered.
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Sep 5, 2024 #4 Welcome to the forum. Just curious, how many of what kind and size of wire, what else in the box, etc?