Dealing with splices from Romex to some of the old BX I realized that metal device boxes are fairly useless. In most cases shorter depth boxes can't be used at all.
1 deduction for clamps in the box
1 deduction for ground wires (up to 4)
2 deductions for a device
so 1 14/2 Romex, 1 14/2 BX, 1 devise, clamps in the box would need 16 cubic inches which would have to be a 3 x 2 x 3.5" box.
Am I doing this right?
I removed my calculation because it contained an error. Note to self don't post after you drank a few Manhattans.
That's only because back then fill requirements were less. Clamps, grounds didn't count and a device only counted as 1. Tails were cut so short so that you could push the device into the box that you barely could wire it. So don't blame the box, blame the guy who used that size box. Larger size boxes were available just as they are today. Cut the box out and replace it with a deep (3x2x3-1/2") metal box.
With new wiring, I always go bigger. It's so nice to be able to easily push the tails into the box and not have to fight with the device. Oh, and I always use metal boxes, not that cheap plastic junk!
-Hal
Second try, coffee only:
NM-14/2=3 conductors
AC-14/2=2
1 Device=2
1 Clamp=1
Total =(8) #14 conductors or 16 cu in.
Minimum size metal boxes: 3 x 2 x 3.5 device box or 4 x 1.125 square box.
Article 314.16 (B) states the steps in 1 through 5. The verbiage can get a little confusing. The 2023 NEC adds a 6th section to the calculation if you have terminal blocks installed in the box. For example, Alumiconns if you are putting copper pigtails from the aluminum wire.