EEC said:According to 210.19(a)4 the circuit conductors can be 14 awg on 20 amp circuit, so why does equipment ground need to be larger than circuit conductor? tail is a bonding jumper 250.146 not installed along with circuit conductors in conduit
(c) Individual outlets, other than receptacle outlets, with taps not over 450 mm (18 in.) long.
EEC said:I am saying it is 20 amp circuit conductors on a multioulet cicuit. Each recapt. load is 180VA
Semantics aside, while a receptacle-to-box connection could be called an EBJ as far as the device itself is concerned, it is definitely the EGC for the equipment supplied by the receptacle.infinity said:Logically the EGC and the EBJ would have to be the same size. If you had a PVC box with a non metallic raceway then the EGC would be sized to 250.122 and terminated on the device. If you're not permitted to install a smaller EGC for that scenario than I don't see how you use a smaller EBJ when bonding to a metal box since they both will perform an identical function.
LarryFine said:Semantics aside, while a receptacle-to-box connection could be called an EBJ as far as the device itself is concerned, it is definitely the EGC for the equipment supplied by the receptacle.
Pierre C Belarge said:The size of the EBJ/EGC is referenced in 250.122.
250.146 is not for sizing the conductor
Pierre C Belarge said:Equipment Bonding Jumpers and Equipment Grounding Conductors perform the same task, and are generally sized the same on the load side of the service disconnect, that is why I used EGC/EBJ in my prior post.
infinity said:I complete agree with you but I can't find the wording in the text of the article 250 to say this. IMO 250.146 should reference 250.122 directly to avoid any confusion.
eprice said:Is 250.102(D) what you're looking for?