I have a job that requires Belden cable to be run to several devices like cameras and other security sytem components. We use Belden cable because all of the devices are 12-24 volts AC.
What is the requirement for sizing the boxes in the conduit runs out to this equipment? Mostly, 1 inch conduit is used. To me a 4 square box would be sufficient for a one or two pair 18 gauge Belden cable. But.........
Article 314.28 A ( Minimum size Pull and Junction boxes and conduit bodies)states that if the conductor is #4 or larger, the following box calculation will be used and so forth.
Ive been arguing this fact for months with other electricians and designers that say if the Belden cable diameter is equal to #4, you have to use this article.
I say BS. Sometimes you have to use some common sense. Belden cable is so flexable, it will go in a 4 square box easy considering there is enough sq inches in the box for that application.
Currently under their rule, the length of the box on a straight pull would have to be 8 times the size of the largest raceway or 8 x 8 x 4 box. This is actually what they are doing on our projects.
There is little to no heating effect by induction in the conduits. Its 24 volts AC and our limit on conduit fill is 25%.
What would be the correct size box to use for these very low voltage conduit runs? Is there anything in the code that would cover this? Article 314 A is the only rule I can find.
What is the requirement for sizing the boxes in the conduit runs out to this equipment? Mostly, 1 inch conduit is used. To me a 4 square box would be sufficient for a one or two pair 18 gauge Belden cable. But.........
Article 314.28 A ( Minimum size Pull and Junction boxes and conduit bodies)states that if the conductor is #4 or larger, the following box calculation will be used and so forth.
Ive been arguing this fact for months with other electricians and designers that say if the Belden cable diameter is equal to #4, you have to use this article.
I say BS. Sometimes you have to use some common sense. Belden cable is so flexable, it will go in a 4 square box easy considering there is enough sq inches in the box for that application.
Currently under their rule, the length of the box on a straight pull would have to be 8 times the size of the largest raceway or 8 x 8 x 4 box. This is actually what they are doing on our projects.
There is little to no heating effect by induction in the conduits. Its 24 volts AC and our limit on conduit fill is 25%.
What would be the correct size box to use for these very low voltage conduit runs? Is there anything in the code that would cover this? Article 314 A is the only rule I can find.