F faresos Senior Member Jun 27, 2019 #1 What size of recessed box needed for 8-wire system furniture infeed? I think 4x4x2 1/8" will work but I thought I just confirm. Thanks!
What size of recessed box needed for 8-wire system furniture infeed? I think 4x4x2 1/8" will work but I thought I just confirm. Thanks!
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jun 27, 2019 #2 What the size and total number of conductors that will be inside the box?
F faresos Senior Member Jun 27, 2019 #3 infinity said: What the size and total number of conductors that will be inside the box? Click to expand... It will be 8 # 12's. I assume the splicing will occur at the junction box above the ceiling before they run it down the wall to the infeed box.
infinity said: What the size and total number of conductors that will be inside the box? Click to expand... It will be 8 # 12's. I assume the splicing will occur at the junction box above the ceiling before they run it down the wall to the infeed box.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jun 27, 2019 #4 According to Table 314.16(A) the box you've mentioned will hold (13) #12 AWG conductors.