When sizing a box for conductors #4 or larger, you need to have 6 to 8 times the conduit diameter plus the diameters of any other conduits on the opposite wall. Do you have to include the diameters of those other conduits if they only have smaller conductors? I'm thinking if you have a junction box with a lot of small conduits for small circuits but then you go add one large one for #4 or larger conductors the box would need to be huge. But all the #14 or #12 wires in the smaller conduits don't really get in the way.