hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
Please see attached sketch. I plans that have pull box that requires volume fill calcs. The pull box has 15 circuits and 4 equipment grounding conductors all #10 enter and leave.
Each circuit is either 120V 1p or 208V 1p. Based on NEC 2014 Section 314.16(B):
Since I have 15 circuits, 2 conductors each thats 30 conductors. Since I have 30 enter and leave thats 30x2=60 conductors total.
The equipment grounding conductor is counted once thus total conductors are 60+1=61.
Based on Table 314.16(B): each #10 is 2.5 in cube.
Thus total volume is 61x2.5=172.5 inch cube.
Would the volume then need to be at least 172.5 in cube correct or incorrect?
Each circuit is either 120V 1p or 208V 1p. Based on NEC 2014 Section 314.16(B):
Since I have 15 circuits, 2 conductors each thats 30 conductors. Since I have 30 enter and leave thats 30x2=60 conductors total.
The equipment grounding conductor is counted once thus total conductors are 60+1=61.
Based on Table 314.16(B): each #10 is 2.5 in cube.
Thus total volume is 61x2.5=172.5 inch cube.
Would the volume then need to be at least 172.5 in cube correct or incorrect?