Where can I find the requirements on this? Is this in the building code or NFPA? I know there are limitations but need some reference. Thanks.
Is there a copy of the current IBC available to view online anywhere?dcspector said:Chevy 03' IBC 712.3.2 membrane penetrations as Bryan mentioned. Also, check "Hilti and Metacaulk-Box Guard" manufs. and In "rated wall assemblies" (min. 1 hr) back to back boxes are not permitted and if they are within 24" of each other then both boxes must be treated with the protective means.
chevyx92 said:Is there a copy of the current IBC available to view online anywhere?