Am I making this up or do you not need to use plenum boxes in a plenum ceiling anymore? Thanks for the help.
The way I read 300.22(C)(3) is that only the non-metallic boxes need to be rated and any metallic box is fine. Am I reading it correctly?300.22(C)(2) (2008) and 300.22(C)(3) (2011) Address equipment located in plenum ceiling spaces. This section requires the use of metal boxes or non-metallic boxes that are listed for use in a plenum.
Chris
My understanding is that in under Chicago code you still need it but for NEC any box is fine.if it actually is a plenum ceiling, not just suspended ceiling, I would still use a plenum box.