Boxes in plenum ceiling

Status
Not open for further replies.
300.22(C)(2) (2008) and 300.22(C)(3) (2011) Address equipment located in plenum ceiling spaces. This section requires the use of metal boxes or non-metallic boxes that are listed for use in a plenum.

Chris
 
300.22(C)(2) (2008) and 300.22(C)(3) (2011) Address equipment located in plenum ceiling spaces. This section requires the use of metal boxes or non-metallic boxes that are listed for use in a plenum.

Chris
The way I read 300.22(C)(3) is that only the non-metallic boxes need to be rated and any metallic box is fine. Am I reading it correctly?
 
As far as I know the only requirement for "plenum" boxes and "plenum" flex is found in the Chicago City Code and in some of the suburban codes in that area. There is no such requirement in the NEC.
 