- Location
- New Jersey
- Occupation
- Journeyman Electrician
Simple question, 225 kva transformer 480-208/120 indoors, secondary condcutor length 40', I say no good limited to 25'. {240.21(C)(6)}
Could it have been installed with 240.92(C) in mind?Simple question, 225 kva transformer 480-208/120 indoors, secondary condcutor length 40', I say no good limited to 25'. {240.21(C)(6)}
Simple question, 225 kva transformer 480-208/120 indoors, secondary condcutor length 40', I say no good limited to 25'. {240.21(C)(6)}
Simple question, 225 kva transformer 480-208/120 indoors, secondary condcutor length 40', I say no good limited to 25'. {240.21(C)(6)}
What is the reason for a limit to conductor length??????????????
Who cares if it's 10 feet or 200 feet? It's still voltage,current etc and the bark and bite are the same too
dick
The six applications covered in 240.21(C)(1) through (6)
permit transformer secondary conductors without an over current
protective device at the point the secondary conductors
receive their supply under one of the following
conditions:
1. The primary over current protective device, as described
in 240.21(C)(1), can protect single-phase (2-wire) and
3-phase (delta-delta) transformer secondary conductors.
2. The transformer secondary conductors do not exceed
10 ft.
3. The transformer secondary conductors do not exceed
25 ft (two applications).
4. The transformer primary plus the secondary conductors
do not exceed 25 ft.
5. The transformer secondary conductors are located outdoors.
Like 240.21(B) for conductors tapped to a feeder,
240.21(C) specifically prohibits application of 240.4(B)
with transformer secondary conductors covered by the requirements
of 240.21(C)(1) through (C)(6). See the commentary
for 240.21(B).
The secondary terminals of a transformer are permitted
to supply one or more than one set of secondary conductors.
The first sentence of 240.21(C) specifies that the requirements
apply to ?a set of conductors supplying a single load?
The basic reason is that the alternative would have been to require protection right at the secondary terminals of the transformer. The important concept is that all conductors must be protected against overcurrent conditions. If you connect too much load to the transformer and wind up overloading the secondary conductors, a breaker at the load end (e.g., the main circuit breaker on the first panel downstream) can open, thereby terminating the event, and protecting the seconday conductors. And that would be true no matter how long the secondary conductors are.What is the reason for a limit to conductor length?
Agreed.Simple question, 225 kva transformer 480-208/120 indoors, secondary condcutor length 40', I say no good limited to 25'. {240.21(C)(6)}
So to directly answer your question, the reason for limiting the conductor length is to limit the probability that a short circuit can take place in that limited length of wire. The longer the wire, the more chances there would be for someone to find a way to run into the wire with a forklift or other heavy object. We keep the run short, and we protect it against damage by enclosing it in conduit, and we accept the (limited) risk that comes from not having an breaker right at the transformer.