BRANCH CIRCIUT SIZING TO AVOID VOLTAGE DROP
mspa
IS THERE A PROBLEM OR VIOLATION WITH OVERSIZING BRANCH CIRCUIT HOME RUNS FOR VOLTAGE DROP ISSUES ON HOME RUNS AND WIRING THE REMAINDER OF THE CIRCIUT IN THE STANDARD SIZE WIRE. EXAMPLE: 15 AMP BRANCH CIRCIUT IS FEED WITH A #12AWG FUSED AT 15 AMP AND THE REMAINDE OF THE CIRCUIT WIRED WITH #14 AWG
Re: BRANCH CIRCIUT SIZING TO AVOID VOLTAGE DROP
No, you can switch to 14 if you want.
Please don't use all capitals, it's hard to read.
[ April 22, 2004, 08:03 PM: Message edited by: russ ]
No problem at all and in some cases a good design! :) It does cause for some confusion for troubleshooters, but overall is better than having excessive voltage drop on the circuit. :)
No problem at all from the NEC.
Some feel this is dangerous as someone might move the 12 AWG onto a 15 amp breaker, you could put a tag on the wire that says 14 AWG down line.
IMO the dangerous part is having unqualified people moving wires in panels. :)
i have an electrical inspector that wants me to rewire an entire house because i did this. i asked him to show me in the code where it is not allowed and his responce was show him where it says it is . he proclaims you can not mix conductor sizes
What is a qualified person any way? Sorry to get off the topic and if the moderators want to move this ok by me
This is a very standard thing to do on larger jobs, I have been on jobs running 4 AWG for 20 amp 120 volt outlets and I can assure your we spliced on smaller conductors to connect to the outlet.
This inspector is mistaken, in my state I could go over his head, I do not know your options.
Bob
I have mixed feelings about changing wire size on the same circuit.
To my thinking from a design consideration is to install a service extension panel closer to the load.
Notice "service extension panel" phrase. ;) My words only.
I simply meant anyone who did not have the sense to check the circuit before changing the ampacity of the overcurrent protection.
Bob
Caj, who would you allow (forget who might) to work in this panel, someone who had a clue, or someone who didn't?
We can't beat idiots even with our best efforts.
Qualified is qualified, this is the reason tests are given covering the whole code book, not just chapters 1 through 4.
As Bryan touches on, many jobs are engineered this way.
Roger
[ April 22, 2004, 08:35 PM: Message edited by: roger ]
Originally posted by mspa:I asked him to show me in the code where it is not allowed and his responce was show him where it says it is.
Try showing him this:
240.4 Protection of Conductors.
Conductors, other than flexible cords, flexible cables, and fixture wires, shall be protected against overcurrent in accordance with their ampacities specified in 310.15, unless otherwise permitted or required in 240.4(A) through (G).
I believe that you have achieved that requirement, by protecting both the #12 and the #14 in accordance with their ampacities. You might also throw this in:
240.4 (D) Small Conductors. Unless specifically permitted in 240.4(E) through (G), the overcurrent protection shall not exceed 15 amperes for 14 AWG, 20 amperes for 12 AWG. . . .
This says you can?t exceed 20 amps for a #12. You haven?t. There is also this:
210.3 Rating.
Branch circuits recognized by this article shall be rated in accordance with the maximum permitted ampere rating or setting of the overcurrent device. . . . Where conductors of higher ampacity are used for any reason, the ampere rating or setting of the specified overcurrent device shall determine the circuit rating.
You have chosen to use a conductor (#12) of an ampere rating higher than that of the circuit (15 amps). That is allowed.
Finally, there is the general notion that if the NEC does not explicitly say that you can?t do something, then you can do that something, so long as that something is not inherently unsafe. However, that general notion does not appear in the text of the NEC itself. So it may be hard to use it in a disagreement with the AHJ.
Gentlemen,
Table 210.24 summarizes Branch Circuit Requirements and specifically states that you can use #14's to tap from #12's. So whether you are tapping as your load reduces or to accommodate voltage drop and size the OCPD @ 15amps, it is acceptable. Hope this helps.
To be clear that part of Table 210.24 only applies to Fixture wires and cords.
See 240.5 and Article 402 Fixture Wires.
You can not tap a 20 amp branch circuit with 14 AWG NM to feed a fixture.
The inspector is wrong, and you do not have to show him anything.
In the states that I work, it goes like this:
By law he must quote to you in writing the CODE Section that he determines that you are violating.
The inspector is not the AHJ. The AHJ is the State or local Fire Marshal who has adopted the NEC. The inspector is, well, an inspector, who is hired to insure CODE compliance.
If the inspector doesn't want to do his job, go to the chief elctrical inspector, and then to the State electrical board.
This is how it is where I work, and could be different for you.
caj1962
No problem asking, although sometimes when we ask a question inside a question it may get lost.
Art 100 Definition of Qualified Person:
One who has skills and knowledge related to the construction and operation of the electrical equipment and installations and has received safety training on the hazards involved.
However, in Article 80 we find information on inspector qualifications (Art 80 has to be adopted by ordinance, but its usefull to look at)
B) Experience. Electrical inspector applicants shall demonstrate the following:
(1) Have a demonstrated knowledge of the standard materials and methods used in the installation of electric equipment
(2) Be well versed in the approved methods of construction for safety to persons and property
(3) Be well versed in the statutes of ________ relating to electrical work and the National Electrical Code, as approved by the American National Standards Institute
(4) Have had at least ____ years? experience as an Electrical Inspector or ____ years in the installation of electrical equipment. In lieu of such experience, the applicant shall be a graduate in electrical engineering or of a similar curriculum of a college or university considered by the Board as having suitable requirements for graduation and shall have had two years? practical electrical experience.
Originally posted by iwire:
"To be clear that part of Table 210.24 only applies to Fixture wires and cords.
You can not tap a 20 amp branch circuit with 14 AWG NM to feed a fixture."
iwire,
I do believe that Table 210.24 applies to branch circuits for lamp holders & receptacles.
Article 210.24
Branch-Circuit Requirements-Summary. The requirements for circuits that have two or more outlets or receptacles, other than the receptacle circuits of 210.11(C)(1) & (2), are summarized in Table 210.24. This table provides only a summary of minimum requirements. See 210.19, 210.20 & 210.21 for the specific requirements applying to branch circuits.
Respectfully submitted :)
I do not agree, but will keep an open mind while others get in on this. :)
[ April 24, 2004, 06:22 PM: Message edited by: iwire ]
I strongly agree with Bob. Table 210.24 is a very poorly designed table and is very misleading, in my opinion. The bottom line is 210.19(A)(2). :)
I would have to agree with the Inspector. I have seen this in commercial, but not in residential. The only reason for this application is voltage drop in big buildings. To see this in houses would scare me. If I did a panel change I would not expect this and would question,"why"?