210.5(C)(1) mentions branch-circuit distribution equipment and panelboards. Since it's differentiated from a panelboard one could assume that it is not a panelboard. Also Branch-circuit distribution equipment is not defined in the NEC so what it is? Would it be something like a PDU?
210.5(C)(1) Branch Circuits Supplied from More Than One Nominal Voltage System.
Where the premises wiring system has branch circuits supplied from more than one nominal voltage system, each ungrounded conductor of a branch circuit shall be identified by phase or line and by system voltage class at all termination, connection, and splice points in compliance with 210.5(C)(1)(a) and (b). Different systems within the same premises that have the same system voltage class shall be permitted to use the same identification.
(a)Means of Identification. The means of identification shall be permitted to be by separate color coding, marking tape, tagging, or other approved means.
(b)Posting of Identification Means. The method utilized for conductors originating within each branch-circuit panelboard or similar branch-circuit distribution equipment shall be documented in a manner that is readily available or shall be permanently posted at each branch-circuit panelboard or similar branch-circuit distribution equipment. The label shall be of sufficient durability to withstand the environment involved and shall not be handwritten.