Jpflex
Electrician big leagues
- Victorville
- Electrician commercial and residential
Is there a code in current 2023 NEC that requires NEW receptacles added or EXTENDING from ungrounded branch circuit receptacle(s) to be required to be a grounded type receptacle along with a GEC connected to the new receptacle and box and the box it is fed from while bonded to the grounding electrode system (assuming there is a grounding electrode system)?
I am aware that a GFCI can replace an ungrounded receptacle to feed another ground type receptacle but not have a EGC between them. (And labels)
I read in an older 2017 bonding and grounding book that said that if a new receptacle is added to extend from existing ungrounded branch circuit receptacles, then an exception could be used to allow a single insulated conductor without conduit or jacket to be ran all the way to the source panel EGC buss and terminated here.
I cannot find this in 2023 NEC code rules. If this still applies, can this single unprotected wire be ran all the way such as in an attic to be terminated to a sub panel ground buss instead of the service buss?
I cannot find this is 2023 NEC. I have purchased the 2023 NEC handbook and under 250.130 C it just says the equipment grounding type receptacle extension must be connected to 1 - 8
1) any accessible point on the grounding electrode system described in 250.50
6) for ungrounded systems the grounding terminal bar within the service equipment enclosure