Branch Circuit Feeders

Status
Not open for further replies.

zodiack

Member
Location
new york
Hey Forum

I am installing a 277/480 service and have a question on wire size.

Long Island

Coming off main service in shopping center and feeding a Trans S Meter Cabinet
Than installing 200 amp / 600 volt Safety switch. 6x6 x4 rain tight trough
Going to fuse switch down to 150 amp ??
I have too run 400 feet to supply and 480 step down transformer. Stepping down to 120/208.
This 120/208 panel are main breaker at 150 amps
I was looking up wire size and at 3% I could run 1/0

The question
Do I have to run full size 1/0. Which is good up to 427 feet at 480 volt delivering 150 amps at the end, or Can I run wire size that is 80 percent of the 150 main breaker in the 120/208 panel
 

zodiack

Member
Location
new york
Wire Size

Wire Size

I know I can run 1/0 wire

Can I size the wire 80 percent of the 150 amp breaker

In turn using a 125 amp fuses in disconnect switch down sizing the wire. to #1 wire
 

richie921

Member
Location
ny,ny
Agreed jumper...where is this sizing the wire to 80% of the OCPD coming from? Is it a misunderstanding of not designing to use more than 80% of a circuits rating? Im confused but no you can't undersized the wire to 80% of the OCPD. In the transformer diagram, I'd prob parallel the secondary instead of 700kcmil but correct as it stands.

Sent from my SM-G935P using Tapatalk
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
You can sort of size the wire to 80% some of the time as follows:
If the load can only be 80% of the breaker rating, then you can size the wires to the load and then possibly use the larger breaker as the next size up from the load current.
Or, depending on the load, you might have to size the wire all the way up to the breaker size to satisfy the 80% rule for the breaker.

Sent from my XT1585 using Tapatalk
 