Branch circuit feeding building
hhsting
Glen bunie, md, us
Junior plan reviewer
See attached sketch. I have bldgs N, B,C. All three buildings are storages warehouse with Bldg B and C smaller in size then Bldg N. Main service disco is at exterior wall of BLDG N. Service disco feeds Panel N inside building N. Panel N feeds thru feeder breaker to Panel C. Panel C has two branch circuits feeding another bldg 50 feet to Bldg B.
panel C is located attached to exterior wall of bldg C. It feeds Bldg C branch circuit lights as well as Bldg B branch circuit lights.
Questions:
1. Would Bldg B need main disco since it has multiple branch ckts? I am aware of 225 but I am not sure it’s confusing since Panel C from which two branch circuits originate is located on exterior walls of Bldg C.
2. Panel C is MLO. Would Panel C not need main breaker? Again it’s confusing it’s on exterior wall attached to Bldg C.
3. Would Panel C need grounding electrode system? Yes I am aware of 250.32 but it’s on exterior wall of Bldg C. So not sure.
All references NEC 2014 please
Thanks for your input
Very hard to follow but you cannot have 2 branch circuits feeding a building unless you meet the exception in section stated above.
If one of those circuits feed the panel in C then it is a feeder so please clarify
Panel C is fed from Panel N in different bldg. Panel C feds 2 branch cuts to bldg B and 2 branch cuts to Bldg C.
Panel C is on the exterior walls of Bldg C. Not sure if Bldg C would have to comply per 250.32 since Panel C is on exterior walls of bldg c is it considered feeder feeding building C, structure or it’s more like feeder feeding panel?
No takers? No one knows?
If your supply circuit lands in a panel and has additional overcurrent devices before supplying individual branch circuits, then that supply circuit is a feeder. See art 100 definitions.