Branch circuit feeding patient bed locations

Status
Not open for further replies.

JLEECME

Member
NEC 2011 517.18A and 517.19A says "The branch circuit serving patient bed locations shall not be part of a multi-wire branch circuit"

If you are running a separate grounded conductor for each ungrounded conductor in the same raceway so as not to have to use handle ties or multiple pole circuit breakers per 210.4 is this still considered a multi-wire branch circuit?
 
NEC said:
Branch Circuit, Multiwire.


A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system.
No
 